Thread: Electrical Requirements for a 4HP spindle

  1. #11
    Join Date
    Mar 2008
    Posts
    84

    Default

    Would there be any benefit placing small rubber pads under the feet of the Bot or just let it rest on concrete?

    Rick

  2. #12
    Join Date
    Mar 2008
    Posts
    84

    Default

    Does anyone have a link to a 90A branch circuit protection breaker that they can provide me for my 4HP single phase spindle? I can purchase online, that is fine with me.

    Regards,
    Rick

  3. #13
    Join Date
    Feb 2008
    Location
    Miller Marine Products, Ridgefield Washington
    Posts
    877

    Default

    If you run the 50 amp breaker to feed your SB the wire needs to be #8 str CU otherwise the wire will melt in half and the breaker will not trip. Breakers protect the wire to small size wire and the breaker will not trip before the wire melts and catches fire. Like was said above you are better off to size the service for the job. It does not hurt to go big on the wire but not small on the wire and big on the breaker.

    Mike

Similar Threads

  1. Electrical and Spindle Experts Help!!
    By Luxury Architectural in forum ShopBotter Message Board
    Replies: 7
    Last Post: 10-28-2011, 05:00 PM
  2. Spindle Power Requirements Needed
    By kenz in forum ShopBotter Message Board
    Replies: 6
    Last Post: 11-10-2010, 09:03 PM
  3. Wiring requirements
    By kubotaman in forum ShopBotter Message Board
    Replies: 1
    Last Post: 09-30-2010, 10:10 PM
  4. Spindle requirements
    By jerry_stanek in forum Assembly & Maintenance
    Replies: 4
    Last Post: 08-09-2009, 10:34 PM
  5. Floorspace requirements
    By rsorensen in forum Archives2007
    Replies: 21
    Last Post: 06-04-2007, 10:05 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •